Sound Attenuation in Ducts due to End Reflection
Sound attenuation from ducts to end terminals due to end reflection for typical duct dimensions with sharp ends and different frequencies are indicated below:
| Duct Dimension1) (mm) | Octave Band Center Frequency (Hz) | |||||
| 63.5 | 125 | 250 | 500 | 1000 | 2000 and higher | |
| 125 | 17 | 12 | 8 | 4 | 1 | 0 |
| 250 | 12 | 8 | 4 | 1 | 0 | 0 |
| 500 | 8 | 4 | 1 | 0 | 0 | 0 |
| 1000 | 4 | 1 | 0 | 0 | 0 | 0 |
| 2000 | 1 | 0 | 0 | 0 | 0 | 0 |
1)The duct dimension is the diameter of round ducts - or square root of area of rectangular duct.
- 1 mm = 0.03937 in
- Noise with lower frequencies are reflected more than sound with higher frequencies
- Rounded terminal ends reflects sound less than sharper ends
- Reflection in funnel shaped ends like trumpets or similar can be nearly neglected
Example - Sound Attenuation from Duct to Terminal due to End Reflection
From the diagram above - the sound attenuation for noise with frequency 250 Hz and duct diameter 250 mm is approximately
4 dB
For the same duct with frequency 500 Hz - the sound attenuation due to end reflection is approximately
1 dB
• Acoustics
• Noise and Attenuation
Sound Attenuation - Duct split to Terminals
Estimating sound attenuation where ducts splits to terminals.
Sound Attenuation in Duct Elbows
Noise attenuation in duct elbows by reflected sound.
Sound Transmission through Duct Walls
Sound transmission from ducts to surrounding rooms.
Sound Transmission through Flanking Paths
Sound transmitted through duct walls, floors and ceilings.
Unlined Sheet-Metal Ducts - Sound Attenuation
Noise attenuation in unlined sheet-metal ducts.
Ventilation Systems - Acoustic Calculation Procedure
Acoustic noise calculation procedure HVAC systems.
Ventilation Systems - Classification of Noise Reduction Silencers
Noise in a ventilation system can be reduced by reactive, diffuser type, active and/or dissipative silencers.