Steam Heating Air
Steam is often used to heat air. Steam condensing rate for air heating equipment can be calculated as
ms = q dt cp ρ / he (1)
ms = rate of condensation, steam consumption (kg/s)
q = volumetric air flow rate (m3/s)
dt = temperature difference in air flow (oC)
cp = specific heat of air (kJ/kg oC)
ρ = density air (kg/m3)
he = specific enthalpy of evaporating (condensation) steam (kJ/kg)
Example - Heating Air with Steam
1 m3/s of air is heated from 10oC to 30oC with steam condensing at atmospheric pressure. The steam consumption can be calculated as
ms = (1 m3/s) ((30oC) - (10oC)) (1.0 kJ/kg oC) (1.204 kg/m3) / (2257 kJ/kg)
= 0.011 kg/s
• Thermodynamics
Basic air changing state processes - heating, cooling, mixing, humidifying and dehumidifying by adding steam or water - psychometric diagrams and the Mollier charts.
Using steam to humidify air.
Air and Steam Mixtures
Air in the steam will lower the surface temperatures in heat exchangers - and less heat will be transferred.
Air Heating Systems
Air heating buildings - heat supply vs. air flow and temperature.
Cooling and Heating Equations
Cooling Load - Latent and Sensible Heat
Latent and sensible cooling loads to consider when designing HVAC systems.
Heating Systems - Steam and Condensate Loads
Humid Air - Heating
Saturated Steam - Properties - Imperial Units
Saturated Steam - Properties for Pressure in Bar
Saturated Steam Table with properties like boiling point, specific volume, density, specific enthalpy, specific heat and latent heat of vaporization.
Steam Consumption for some Typical Steam Heated Consumers
Steam consumption rates for typical steam heated consumers in industries like bakeries, breweries, paper factories etc.
Steam Heating Systems - Classifications
Steam systems carries heat through pipes from the boiler to consumers as heat exchangers, process equipment etc.