Hazardous Areas - Protection Techniques according European IECEx
Electronic or electrical equipment of any type for use in European hazardous areas must be ATEX certified as required by the EU directive 94/9/EC - also known as the ATEX directive.
Basis for equipment certification is the hazardous area classification system used, the
Ex marking
The ATEX directive classifies equipment into groups and categories which are defined by the marking on the equipment. A typical marking can be
Ex Classification - Equipment Marking
0158 II 2G EExd IIB T4
EU
Directive
Notified
Body
Code
Explosion
Proof
Equipment
Group
Category
Gas/Dust
Type of
Certificate
Type of
Protection
Group
Sub Group
Temperature
Classification
The different parts of the nomenclature are explained below:
CE Mark
Informs that the product complies with the European Directive.
Notified Body Code
Informs witch official Notified Body did the testing and certification of the product.
Explosion Proof
The explosion proof Ex tag is required for certified equipment in accordance with the ATEX directive.
Equipment Group
The tag for equipment group relates to groups in the Zone system where
  • I - is for use in underground mines
  • II - is for all other places
Category - Gas/Dust
Category
The tag for category relates to the Zone in the Zone system where
  • 1 - is for equipment for use in areas where an explosive atmosphere is present continuously or for long periods or frequently
  • 2 - is for equipment for use in areas where an explosive atmosphere is likely to occur in normal operations
  • 3 - is for equipment for use in areas where an explosive atmosphere is unlikely to occur in normal operations
Gas/Dust
  • G - equipment certified for flammable gases
  • D - equipment certified for dust atmosphere
Type of Certificate - Type of Protection
Type of Certificate
Types of certificate indicates standards used for the certification.
  • EEx - European standards
  • AEx - American standards
Type of Protection
Types of protection indicates the level of protection concepts the equipment is designed for. The protection concepts are divided in to sub classes.
Encapsulated
Protection applied by encasing the components in a resin type material.
The protection is referred to as "Ex m".
Sub divisions ma for Zone 0 and mb for Zone 1.
Flameproof
The enclosure can withstand the pressure developed during an internal explosion of an explosive mixture. The explosion is not transmitted to the explosive surrounding atmosphere and the enclosure operates with a temperature to low for the surrounding explosive gas or vapor to ignite.
This protection is referred to as "Ex d".
Intrinsically Safe
Electrical equipment is under normal or abnormal conditions incapable of releasing sufficient electrical or thermal energy to cause a ignition of the hazardous surrounding atmospheric mixture.
This protection is referred to as "Ex i".
Sub divisions ia  for Zone 0, ib for Zone 1 and ic for Zone 2.
Increased Safety
High quality and very robust components. Various measures are applied to reduce the probability of excessive temperatures and the occurrence of arcs or sparks in the interior and on the external parts of the equipment. Increased safety may be used with flame-proof type of protection.
The protection is referred to as "Ex e".
Oil Filled
Protection applied by submerging the components in oil.
The protection is referred to as "Ex o".
Pressurized/purged
Protection applied by keeping a positive pressure in the enclosure relative to the surrounding atmosphere with air or an inert gas. With an overpressure monitored, maintained and controlled - the surrounding ignitable atmosphere can not come in contact with energized parts of the apparatus.
The protection is referred to as "Ex p".
Sub divisions px or py for Zone 1 and pz for Zone 2.
Sand/Powder/Quartz Filled
Protection applied by covering the components with sand, powder or quartz.
The protection is referred to as "Ex q".
Non Incendive
A protection applied to electrical equipment in such a way that normal operation is not capable of igniting surrounding explosive atmospheres.
The protection is referred to as "Ex n".
Special Protection
Any method which can be shown to have the required degree of safety.
The protection is referred to as "Ex s".
Group - Sub Group
  • IIA - Atmosphere containing propane, acetone, benzene, butane, methane, petrol, hexane, paint solvents or gases and vapors of equivalent hazard.
  • IIB - Atmosphere containing ethylene, propylene oxide, ethylene oxide, butadiene, cyclopropane, ethyl ether, or gases and vapors of equivalent hazard.
  • IIC - Atmosphere containing acetylene, hydrogen, carbon disulphide or gases and vapors of equivalent hazard.
  • IIIA - Atmosphere containing combustible flyings.
  • IIIB - Atmosphere containing non-conductive dust.
  • IIIC - Atmosphere containing conductive dust.
Temperature Classification
Hazardous area equipment is classified according to maximum surface temperature produced under fault conditions at ambient temperature 40 oC (104 oF), or as otherwise specified.
Ex Classification - Temperature Codes
Temperature CodeoFoCTypical Substances
T1 842 450 Hydrogen, Toluene, Ethyl acetate
T2 572 300
T3 392 200 Petrol, Gasoline, Diesel
T4 275 135
T5 212 100
T6 185 85
Risk, Reliability and Safety
CE Marking
Verifies that a product is designed to the appropriate standards according the European Machine Directive.
Chemicals Hazard Rating System
The National Fire Protection Association (NFPA) hazard system for chemical materials.
Dust Explosions - Substances, Critical Temperatures and Concentrations
Critical temperatures and concentration parameters for substances like coal, zinc, uranium and more.
Hazard vs. Flash Points
The flash point of a chemical indicates how easy it may ignite and burn.
Hazardous Areas - European Classification Standard
European hazardous area classification with zones, protection types, temperature codes and codes.
Hazardous Areas - North America Classification
North American hazardous locations classification with classes, divisions and groups
Hazardous Areas Protection Techniques for North America
Dust-ignition proof, explosion proof, instrinsically safe and nonincendive protection of hazardous areas.
IP - Ingress Protection Ratings
IP - Ingress Protection rating is used to specify the environmental protection - or electrical enclosure - of electrical equipment.
Water Sprinkler Protected Areas vs. Hazard Classification
Maximum fire sprinkler protected area vs. classification and construction.